  1. Talked to Altronix today - they said the ripple is a typical amount, and that their supplies MUST be used with cameras that have isolated supplies. He said that it will not adjust down to 12V even though it is a 12V supply because it is the battery backup version.

     

    He also said if I used one of their "CCTV" supplies it would have the same ripple amount.

     

    Really, if a camera has isolated supplies it can be run off of 24VAC...

     

    So, it is operating as it is supposed to. In the pic you can see the devices that are not even bolted to the heatsink - just stuck with adhesive material. The one that is attached is with a rivet.

     

    This is not a good long term reliable solution. At least it has a UL listing which is more than most of the inexpensive supplies out there have.

     

    May post a video later of me taking a 40lb sledge to this thing. Luckily there is enough room inside for a good linear like power-one or acopian. This thing is not even in that league. I've never seen a switcher this noisy.

    0530021835.thumb.jpg.1425aca26f56453e68a61bae7bc098b6.jpg


  2. Ground Loop? I have purchased a whole lot of altronix and have had no problems. Supplier stands behiind them if a return is necessary. Could be someone used a alstonix box and put a cheap/defective power supply and threw it out on ebay.?

    Nah, there's to many details that are correct charger connection, 12/24V select, status relays etc. I suppose could be a bad supply, but I don't think the guy would do that - perfect feedback. I'll give Altronix a call tomorrow and see how much ripple this puppy is supposed to have.


  3. Picked up a AL600ULPD8CB (new, via ebay) to power the "cheap" cams (CNB etc), to make it look a little more finished than my HP linear supply.

     

    Now have faint wavy lines in the picture...

     

    And the supply can only be adjusted down to 12.6V.

     

    Did not hook up a battery, I would not think that was related.

     

    Gotta admit, I'm not that impressed with the construction either. Some of the devices are not even screwed to the heatsink, just stuck on with sticky material. The one device that is firmly attached is via a rivet...

     

    I'm sure I can add resistors to the circuit to get the voltage right, but these wavy lines suck.

    Any ideas appreciated.


  4. Some cameras you can get multiple streams, and depending on the VMS does not have to be viewed at full res. In addition to what has been mentioned, I know that Axis ACS allows you to define based on the number of cameras the different frame rates image size etc that is in live view. Also bandwidth will depend on the type of encoding, for example on live view you could do mjpeg or mpeg4 etc. This is independent of the stream being recorded.


  5. Did you have a look at the display adjustments?

     

    Digitally zoom into the image and see what happens

    That was they key. Right clicked on the picture, changed brightness from 0.98 to 1.00 and problem solved. Tried exiting and restarting the client to see if it saved and it does (as one would hope).

     

    We also had tried playing with the settings the other night, but mostly just rough adjustments and not on the last 2% of the brightness scale. Then got hung up reading the manual about camera settings.

     

    Thanks!

     

    P.S. Digital zoom did not seem to make a difference in the brightness, unless it is changed to 1.00 first.


  6. Anyone know how to disable this feature? Looks "brighter" but overexposes faces at night, to the point where you cannot see any detail.

     

    Camera (Axis P3346) looks perfect on other VMS. On Axis camera station, the image enhancement is off by default, and can be controlled by a slider. Looks perfect on Milestone too.

     

    Reading the manual I cannot seem to find the settings they mention, perhaps this feature can only be adjusted with Avigilon cameras?

     

    Thanks in advance.


  7. May provide more than an amp for example depending how the protection is setup, and the exact nature of the overload.

     

    Keep in mind not all these cheap supplies are UL listed - and may very well be a fire hazard when overloaded. What UL refers to as sustained flame, as opposed to a little smoke.

     

    Not a good idea. You can get the correctly rated supply fairly inexpensively, and give yourself some margin - don't run a 2A supply at 2A.

×